2016-10-06 12 views
0

zabbix에서 온도 cpu 사용에 적합한 OID를 찾고 싶습니다. 명령 snmpwalk를 사용합니다.omreport 명령 및 snmpwalk 명령과 다른 결과

#snmpwalk -c public -v2c 127.0.0.1 .1.3.6.1.4.1.674.10892.1 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.8.1.1 = STRING: "Mainboard MB Temp" 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.8.1.2 = STRING: "Front Panel FP Temp" 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.8.1.3 = STRING: "BP Temp" 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.8.1.4 = STRING: "CPU0 Temp" 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.8.1.5 = STRING: "CPU1 Temp" 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.8.1.6 = STRING: "DIMM Temp" 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.8.1.7 = STRING: "IOH Temp" 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.10.1.1 = INTEGER: 750 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.10.1.2 = INTEGER: 500 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.10.1.3 = INTEGER: 550 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.10.1.4 = INTEGER: 1020 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.10.1.5 = INTEGER: 1020 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.10.1.6 = INTEGER: 1000 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.10.1.7 = INTEGER: 1050 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.11.1.1 = INTEGER: 700 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.11.1.2 = INTEGER: 450 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.11.1.3 = INTEGER: 520 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.11.1.4 = INTEGER: 980 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.11.1.5 = INTEGER: 980 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.11.1.6 = INTEGER: 950 
SNMPv2-SMI::enterprises.674.10892.1.700.20.1.11.1.7 = INTEGER: 950 

온도 CPU 1과 CPU 2에 대한 OID는 매우 높습니다. zabbix에서 사용해야하는 가치는 무엇입니까?

omreport 명령

#omreport chassis temps 
    Temperature Probes Information 

    ------------------------------------ 
    Main System Chassis Temperatures: Ok 
    ------------------------------------ 

    Index      : 0 
    Status     : Ok 
    Probe Name    : Mainboard MB Temp 
    Reading     : 44.0 C 
    Minimum Warning Threshold : [N/A] 
    Maximum Warning Threshold : 70.0 C 
    Minimum Failure Threshold : [N/A] 
    Maximum Failure Threshold : 75.0 C 

    Index      : 1 
    Status     : Ok 
    Probe Name    : Front Panel FP Temp 
    Reading     : 17.0 C 
    Minimum Warning Threshold : [N/A] 
    Maximum Warning Threshold : 45.0 C 
    Minimum Failure Threshold : [N/A] 
    Maximum Failure Threshold : 50.0 C 

    Index      : 2 
    Status     : Ok 
    Probe Name    : BP Temp 
    Reading     : 21.0 C 
    Minimum Warning Threshold : [N/A] 
    Maximum Warning Threshold : 52.0 C 
    Minimum Failure Threshold : [N/A] 
    Maximum Failure Threshold : 55.0 C 

    Index      : 3 
    Status     : Ok 
    Probe Name    : CPU0 Temp 
    Reading     : 80.0 C 
    Minimum Warning Threshold : [N/A] 
    Maximum Warning Threshold : 98.0 C 
    Minimum Failure Threshold : [N/A] 
    Maximum Failure Threshold : 102.0 C 

    Index      : 4 
    Status     : Ok 
    Probe Name    : CPU1 Temp 
    Reading     : 78.0 C 
    Minimum Warning Threshold : [N/A] 
    Maximum Warning Threshold : 98.0 C 
    Minimum Failure Threshold : [N/A] 
    Maximum Failure Threshold : 102.0 C 

    Index      : 5 
    Status     : Ok 
    Probe Name    : DIMM Temp 
    Reading     : 51.0 C 
    Minimum Warning Threshold : [N/A] 
    Maximum Warning Threshold : 95.0 C 
    Minimum Failure Threshold : [N/A] 
    Maximum Failure Threshold : 100.0 C 

    Index      : 6 
    Status     : Ok 
    Probe Name    : IOH Temp 
    Reading     : 72.0 C 
    Minimum Warning Threshold : [N/A] 
    Maximum Warning Threshold : 95.0 C 
    Minimum Failure Threshold : [N/A] 
    Maximum Failure Threshold : 105.0 C 

영어로 불편을 끼쳐 드려 죄송합니다.

답변

0

Dell에서 MIB 파일에 따라 사용되어야한다

이 속성은 temperatureProbeTypeIsDiscrete가 아닌 다른 유형의 온도 프로브에 대한 독서를 정의 :이 MIB 개체의 상태에 대한 설명 iso.org.dod.internet.private.enterprises.dell.server3.baseboardGroup.thermalGroup.temperatureProbeTable.temperatureProbeTableEntry.temperatureProbeReading.입니다 1.3.6.1.4.1.674.10892.1.700.20.1.6. temperatureProbeType의 값이 temperatureProbeTypeIsDiscrete가 아닌 경우이 속성에 대해 반환되는 값은 프로브가 섭씨 10도에서 읽는 온도입니다. temperatureProbeType 값이 temperatureProbeTypeIsDiscrete 인 경우 값은이 속성에 대해 리턴되지 않습니다.